LED on 3 phase system with 2 multiplus II in parallel on each phase

I have built the first 3-phase system with 2 MP-II in parallel on each phase and I would like to get a confirmation whether the LED lighting is as should be as there is different LED light combination on multipluses within each phase.


When the system is set to Bulk, the LED lights indicate as follow:


Inverter #1 on L1 lights: Main on, bulk on, inverter flashing

Inverter #2 on L1 lights: Main flashing, inverter flashing

Inverter #3 on L2 lights: Main on, bulk on, inverter flashing

Inverter #4 on L2 lights: Main flashing, inverter flashing

Inverter #5 on L3 lights: Main on, bulk on, inverter flashing

Inverter #6 on L3 lights: Main flashing, inverter flashing


Thank you for your comments.

3 phaseled
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@jaro2k

Get a GX. Save yourself headaches.

There is also the Victron toolkit app. So download that on your phone.

Lights sound correct BTW.

One flashing master, one flashing slave on each phase.