My loads max out at around 150amps but mostly around 50amps. İs it ok to use the 250amp.mega fuse for the main fuse on the lynx shunt?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
My loads max out at around 150amps but mostly around 50amps. İs it ok to use the 250amp.mega fuse for the main fuse on the lynx shunt?
The Lynx uses a CNN fuse type. I think the dimensions are a little different, so no. You can find some class t fuses that fit there as well. Basically is needs to match the dimensions. CNN dimension is the top picture.