Multigrid Three Phase

We have a client with two Multigrid 24/3000 units in parallel and we need to upgrade it to three phase, is it possible to use a multiplus for the additional inverter or does it have to be a Multigrid, system is offgrid so the dual relays are not required?

multiple inverters
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

All units need to be the same. A MultiGrid can't be used together with a normal MultiPlus.

You need to find another (used) MultiGrid or change all to new MultiPlus.