So far I have tried the tips & tricks from the other posts but I have two problems occuring:
1. BMS does not show in cerbo GX
2. When I connect the CAN to the Cerbo, the BMS loses directly the communication with the connected CAN cel module and it's cells.
What I have tried so far:
- Connect pin 7&8 (RJ45) to CanH and CanL of BMS & connect pin 3 to GND
- Connected 120 Ohm at BMS side and used the Victron termination at cerbo side, when measuring I measure a good 60 Ohms.
- Tried all CAN speeds, however I know I need 500kbs
- Tried EMUS firmware 2.10-victron, 2.9.2-victron, 2.9.1-victron
- Tried VE.BUS & VE.CAN and set VE.CAN port to 'CAN-Bus BMS (500kbit/s)'
The network status does show that there are packages delivered, however they are all errors.
I ordered a CAN splitter (or filter), hope that will help.. but Im kinda out of options.. Anyone?