question

Shane Granger avatar image
Shane Granger asked

Blue Power Panel strange amp readings

Installing a multiplus 12/3000 with v.net battery controller and blue power panel. System appears to be functioning properly but the overview screen gives me a consistent 9-10 amp drain even with no load. By that I mean completely disconnecting any loads from the battery switches forward. Anyone have a suggestion? I'm fresh out of ideas.

MultiPlus Quattro Inverter Chargerblue power panel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi Vegall,

Double check the wiring of the VE.Net Battery Controller, and try with the system side of tue shunt totally disconnected.

Make sure the shunt is in the minus.

If that doesn’t help, I recommend to contact your dealer, ie follow official support channel:

Www.victronenergy.com/support