I have some problems with the frequency shift of my MultiPlus ii-GX 5000/48/70-50. When the battery is nearly full my BMS reduces the CCL until it reaches 0. Unfortunately the MultiPlus does not shift the frequency enough to reduce the PV power. This results that the BMS blocks charging, there is a little voltage spike, a lot of electronics crash and then the MultiPlus switches to 51.54 Hz to shutdown the AC coupled PV inverter.
So my question now is, why is the whole range from 50.30 Hz - 51.50 Hz not used, to slowly reduce the power and shutdown the AC coupled inverter BEFORE the BMS cuts off the battery for loading?
MultiPlus II-GX firmware: 508
ESS Assistant version: 018C
In the GUI under DVCC only DVCC is enabled and the correct BMS is selected.
Batteries: Custom made LFP 18S with JKBMS with dbus-serialbattery (I'm one of the developers)
An additional question to the "Frequencies" and "Total solar power" page. Below 50.20 Hz (in my case) it should be 100% solar power and 51.20 Hz should be 0% solar power?
Is it using:
1) The total installed PV inverter power of 5000 W for 100 %
2) The total installed panel power of 6480 W for 100 %
3) The last seen power when frequency was below 50.20 Hz
Probably it is even more complex. I try only to understand why the system is not frequency shifting as it should.
Let me know, if I forgot any important informations.