How many devices to connect to Lynx Power In ?

Hello,

I am currently purchasing and procuring items for my solar install. The setup is as follows:

1. 22 Longi 570W panels (12 panels on the 100A, 10 panels on the 85A)

2. Two Victron SmartSolar Charge Controllers (150/100A, 150/85A)

3. Victron Multiplus II 5000/70 (230v)

4. Midnite Solar Combiner Box MNPV6

6. 48v 280ah Battery Box from Shenzen Deriy

7. Battery Monitor BMV-712

8. Cerbo GX

I have been trying to find the best way to connect everything together as my funds have been severely depleted using the Lynx Power In and wanted to inquire if i can use the Lynx Power In to connect the two charge controllers, inverter and battery box all on one bus bar. I will place the BMV-712 after the Lynx Power In and a DC MCCB the Battery Box to serve as a disconnect. Can i connect them all together without fuses ? If i need fuses, can i place two fuses for one side and no fuses for the other side but all on the same bus bar ? Thank you all.

lynx distributor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@samir101ng

It can take 4 in. 2 mppts an inverter and a battery connection is it.

You can technically do 6 if you use the ends as well.

There is a modification (Google it) to adapt the lynx to take mega fuses so each connection can have one. Ideally you do want fusing.

See the picture on the product page.