question

frankvw avatar image
frankvw asked

Multiplus input/output separation

Quick question: is it alright for a Multiplus charger/inverter to use a common (shared) neutral and earth wire on the input and the output, or must the input and output always have separate neutral and ground wires and may these not be connected?

Multiplus-IIwiring
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Duivert NL avatar image
Duivert NL answered ·

Hi, always separate!

Would otherwise not be safe when grid fails

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.