Hi,
on my Multiplus2 GX I switched the CAN to BMS CAN (500k) and it properly detects my Pylontech battery.
Yet in the status I see this:
After like 2mins of operation, TEC begins to rise until state turns to ERROR-WARNING and subsequently to the seen ERROR-PASSIVE. I can see all battery data coming in nicely and also hooked a oscilloscope to the CAN to see what's going on. I can see the battery's msgs being acked by the GX and (a lot less) msgs from the GX being acked by the battery. I don't have the means to check if every msgs by the GX is acked by the battery, but the ones I could trigger on where acked.
To my understanding the CAN works fine at least on the Layer2.
Any clue why the GX goes into ERROR-PASSIVE then and reaches high TEC counts?
Thanks in advance!