Hello Everyone,
What is the reason for making a high internal temperature alarm on Lynx Shunt?
Any recommendations? Might it be loose connections or so?
Thanks in advance
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello Everyone,
What is the reason for making a high internal temperature alarm on Lynx Shunt?
Any recommendations? Might it be loose connections or so?
Thanks in advance
Loose connection, poor ventilation especially if something has fallen over the slots or the fuse starting to get hot under high current flow. There was a case on here of someone with an overheating Lynx Shunt because their fuse was rated too close to their normal continuous current, the fuse should be 25% higher than max continuous current demand.