Hi I’ve had a multiplus ii 5000 system installed last year with 2x us5000 pylontech batteries working fine with ESS , today a installed my solar panels 10 x longi 425w 2 strings of 5 both strings tested with multimeter at the mc4 connectors and have 187v on both strings but my mppt still says 0v and remains in off position ? Is there any settings I need to change for it to turn on , there is only the blue bulk led flashing


img-1760.png

MPPT SmartSolar
img-1760.png (195.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

If you have 0V PV, then something is off in your PV wiring.

I would carefully check that and use a meter to verify it is ok.

It's state is "on" because it is being powered by the battery.

Check any fuses and switching in the path.