Hello together,
I am testing DESS from the beginning, each verison. Unfortunatelly not so intensively bacuse the system still needs from my point of view improvements to be fully developed.
I see mainly these troubles with:
1. not possible to setup different SOC for DESS calculations and further usage of the battery
2. DESS does not respect grid set point - eg. -200W in case of no import, no export
3. System calculate only till 00:00 as is should be the end of the world....:)
I belive that all these points are already well adressed and will be solved soon :)
Main problem I have with the export power. The system is exporting almost 12kW and I have specify max export power to 6kW, also I tried to modify max. discharge power to 6kW. No improvemt, still exporting full speed. Only solution is to limit max. geed-in in ESS to 6kW. That is what I am using just now.
But this is not what I want. In case that battery is full I want to feed in all PV power. Over 6kW will be used by heating system....but for DESS calculation I need to keep specified limits....
latest v3.3-18, ESS updated.
portal ID> 48e7da891f5b
Thank for feedback.