How can i calculate that three (3) or more 220AH Victron batteries can be connected to 12V/1600VA/70AMP Victron inverter.

battery capacity
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
wkirby avatar image
wkirby answered ·

I am not too sure what you want to calculate.

Three (3) 12V 220Ah batteries should be connected in parallel to maintain a system Voltage of 12V to use with a 12V inverter. You will have 660Ah in that case.
If the MultiPlus is charging at 70A from 50% SOC then it will take ~5 hours or more to reach 100%.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

isaac-coffie avatar image isaac-coffie commented ·

CAN i connect 8 batteries


0 Likes 0 ·
isaac-coffie avatar image isaac-coffie commented ·

what will be the cause if i connect 8 batteries

0 Likes 0 ·
Justin Cook avatar image
Justin Cook answered ·

You can connect as many batteries as you want, @isaac coffie. So long as they are in parallel, maintaining 12v, the number of batteries connected is irrelevant other than increasing the time needed to charge the bank. Your inverter neither knows nor cares how many batteries are connected in parallel to it.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

A lead acid battery should be charged with 10-15% of the capacity. -> 100Ah battery -> 10-15A charging current

Your Multi can charge with 70A max. -> up to 700Ah of batterys.