Hi all,
I have had a problem for the last years with our systems SOC and made some progress, but could not resolve it completely, so any help is greatly appreciated.
As the title states, our VE.Bus SOC is stuck at 85% after absorptions stopped.
I'm fairly sure that it recognizes that Bulk has stopped, as the SOC jumps from something around 70% to 85% when the absorption voltage has been reached.
Insofar I was successful to implement the steps described here: https://community.victronenergy.com/questions/823/why-is-my-maximum-soc-stuck-at-85.html
Now the problem is that after jumping to 85% the systems SOC does not add anything up to the value defined in VE Configure, not by calculating nor by recognizing that the charger is in float mode.
The system is an offgrid-system,
Batteries 6x 2 V 800 Ah OPZS
BlueSolar Charger MPPT 150/70 (v1.61)
MultiPlus 12/3000/120-50 (510)
CCGX (v3.22)
Any help would be greatly appreciated, as our victron specialist is unresponsive and gave false and contradictory information. This is the last resort to have a somewhat reliable SOC.
Thanks!
Edit:
Today it seems to work, after it showed the behavior described above yesterday. I'm still puzzled about yesterday's display, I'll attach an image with relevant information.
I'll leave the post up for anybody having the same issue, as far as I understand I just had to wait one day.