VE.BUS has stopped reporting AC1 power

All was fine on my Multiplus-II 12/3000/120-50 until I repeated a test during which I unplugged the unit from the grid. As expected L1 data went to zero. After I restored power, the L1 power data remained at zero, even after the unit has gone to Float. I tried doing a VE.BUS restart, no change.

Note this is being reported by the Cerbo. To eliminate it from the problem, I direct cabled the MK3-USB into my PC and cranked up VE Configure:

1710008442680.png


Note the 0VA power and IMains number, although voltage is being shown. Given that I'm typing this via a connected computer that is drawing ~300W, these numbers are wrong (that, and the numbers reported correctly before I did the grid outage test scenario). Other statistics appear to be fine.

VictronConnect, via the MK3-USB, is showing the same thing:

1710008850381.png


Per Cerbo screens, this is Product ID 2705 at firmware level 508

How can I recover?


VE.Bus
1710008442680.png (119.9 KiB)
1710008850381.png (61.6 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevinc-63559 avatar image kevinc-63559 commented ·

ps. Tried a full system power cycle via the on/off switch. No change.

pps. Was playing with Grafana (I know, not supported), but noticed two things. One, it was reporting at one point: 1710012259025.png

and two: Per the influxdb, the values are currently simply not being supplied. e.g. influxdb has no data points for AC L1 In power.

0 Likes 0 ·
1710012259025.png (15.1 KiB)
1 Answer
kevinc-63559 avatar image
kevinc-63559 answered ·

Apparently the pins in the Current Sense connected needed resetting. Inserted an appropriate size probe and the problem went away.

img-1754.jpg


img-1754.jpg (3.6 MiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevinc-63559 avatar image kevinc-63559 commented ·
Should have mentioned: This solution was compliments of Dexter over at Current Connected, who responded to my concerns on a Saturday night! Great service!