I hawe alarm "lov battery voltage" on 51V check on battery. In manual i read 38V. Instalation don't start. What i can do? Instalation work when sun light and voltage go to 53V with mppt 250/60 smart solar controller. Ewrything its new.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I hawe alarm "lov battery voltage" on 51V check on battery. In manual i read 38V. Instalation don't start. What i can do? Instalation work when sun light and voltage go to 53V with mppt 250/60 smart solar controller. Ewrything its new.
I found problem. Its virtual switch. It's set on "drive multifunctional". When i set it to ”do not use” the alarm has disappeared. I have an island installation.
Alarm setpoint on dc, programed properly on 41,2 V off, and start on 47V. I didn't change.
Now evrything works.
Thx, it's always good to ask someone.
Hi Janusz. It's a little strange that your unit has arrived programmed for a low V much higher than the typical default. Perhaps the supplier has done this? If so, ask him to fix it. You can do it yourself though:
https://www.youtube.com/watch?v=V1Zceq02vMA
Note you'll need a computer and a MK3/usb adaptor. Maybe your supplier could send you a 'loaner' if he's distant and you don't want to spend more.
If you happen to have a GX box and VRM access then it can be done via VRM too.
I try to do it my self, mk3/usb adaptor i will have in next week.