Extention of system with second mppt rs 450 100

Can I add and how second 450/100 RS to my 35KW batteries - 7 US5000



mppt rs
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
snoobler avatar image
snoobler answered ·
  1. Connect second RS 450/100 to DC bus with suitably sized cables.
  2. Assuming you have VE.Can communications with a Cerbo or other GX device. Remove blue terminator plug from first RS450/100 and move to second RS450/100. Connect second RS450/100 to first RS450/100 with CAT5 ethernet cable.
  3. Connect second array to second RS450/100 with suitably sized cables.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image
snoobler answered ·

I don't think the VE.Can MPPT have to be the same model, so it should work just like a RS 450/100.


The lower voltage of the 250/100 will require lower array voltage but can use much higher current arrays.


Connections would otherwise be the same.