I Need to program one of the relays in Multiplus 2 to get the battery low voltage signal. Need to change it to off when battery is fully charged.
I have the Cerbo GX also. If it is possible by Cerbo GX, that’s ok.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I Need to program one of the relays in Multiplus 2 to get the battery low voltage signal. Need to change it to off when battery is fully charged.
I have the Cerbo GX also. If it is possible by Cerbo GX, that’s ok.
What you are looking for is the two signal BMS support assistant.
Open VE config in demo mode and have a walk through and see the options and if they suit you.
Very simply though if you program the inverter to charge to the correct voltages and amps then you will be ok. The BMS should only shut the system down if there are problems.
Couldn't find the solution. I wants to know how to set the relay on Multiplus II to get the overload condition of the inverter. I cannot see and document for this.
Regards,
Rabeendra.
There are lots of options in the Programmable Relay Assistant which you can load using VEConfig.
For example this one: