Hi, I have a 3x250A main connection. Can I use the VM-3P75CT with ct's with a higher rating? E.g. current ratio 250:5?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi, I have a 3x250A main connection. Can I use the VM-3P75CT with ct's with a higher rating? E.g. current ratio 250:5?
Idoes is correct. The CTs that come with the VM-3P75CT cannot be changed. Victron calibrates/ tunes them for the meter they are ship with. The larger CTs would overpower the meter. I would recommend looking at the EM530 from Carlo Gavazzi. I purchased my Energy meter with the 250-amp CTs included. The unit is working great. The EM530 is lots faster compared to the EM24 from Carlo Gavazzi.
Thank you Mr Orange and Idoes. Two questions please: 1) what does the reporting information display look like from the EM530 to the Cerbo-GX Screen and VRM? is there any missing data that the 3P75CT captures/displays? 2) Are there any plans for Victron to release additional CTs for the 3P75CT? (100A?, 150A?, 200A?)???