What busbar to use to join dual parallel multiplus AC outs

I am building a parallel multiplus and wondering what people generally use to join the outputs before going to panel (which is 30ft away). None of the victron busbars I see are rated for that voltage and all diagrams generally just show nothing. I am using dual 24/3000/120V multipluses

screenshot-2024-03-02-at-30507pm.png

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@happycloud

That will be because AC distribution is based on local regulations.

Look for something like this based on your amps needs. Or this.

FYI though the longer your AC cable it the loads balance better on parrallel set ups so don't join them too close. In the three phase parallel manual it recommends using slightly lower gauge cable and a little bit longer.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

happycloud avatar image
happycloud answered ·

Thanks - but these are not standalone and meant to be in a panel which is a bit overkill to join two wires together

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
Yeah. Just examples. Fairly certain you can look for what you want.