3 x 10kWh Byd Bbox
Full sunshine today and client batteries only went up to 72%
This system is capable of producing 50kWh in a day. Please give advise as too issue.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
2 x 150/100 MPPTs
3 x 10kWh Byd Bbox
Full sunshine today and client batteries only went up to 72%
This system is capable of producing 50kWh in a day. Please give advise as too issue.
Hello,
In order to evaluate if there is an issue it is necessary to confirm if the MPPT haven't charged the batteries whilst there was excess of PV generation. And if that's the case please check in the history of the system (you can download this from VRM) what was the CCL at the time. This will tell you which of the devices decided no to charge the battery