I have a Multiplus GX with two Mppts and an external AC inverter controlled by a JK BMS with Can (pb2a16s15p). All battery values appear in the remote console. As soon as I reach 100% Soc the BMS switches between charging and discharging every few seconds. The level of charging/discharging is also different, +-5A, +-10A, up to +-30A. If I switch off the MPPTs, the Multi only takes 1-2A from the AC inverter, but even then charging/discharging occurs around the float/charge end voltage. If I take out the float mode in the JK bms, the voltage applied to the RCV increases but there is also charging/discharging. Why does the float/charge voltages overshoot and then have to be regulated down by discharging??? It's also strange that in the morning my battery jumps from 50% SoC to 95%-100% SoC within 30 minutes. I only charge with 65a so there's no way it's full. The voltage doesn't match 100% either, it increases from almost 52.0v to 54.0v. I have Soc in BMS on 55.2 so 100% shouldn't actually be displayed. There is even discharging of the battery while exporting to the grid. (see picture) mpps deliver 3.2kw, the inverter dicharges with 1.3kw all while the AC coupled inverter exports 5wk at the same time BMS setting and VRM screenshot in which you can see the SOC jump yesterday morning from 8:00 to 8:30 (this happens pretty much every day).