VRM False alarm

I have a shunt configure as DC load, I have an "High voltage alarm" reported by VRM that's keep coming even after I cleared it.

Cerbo GX firmware v3.20

screen-shot-2024-02-19-at-93440-am.png



The alarm is not configured to be active

screen-shot-2024-02-19-at-93521-am.png


The voltage on this shunt is normal, 13.58V as indicated in the photo below ( not above the high voltage threshold )


screen-shot-2024-02-19-at-95104-am.png


Where this alarm comes from and how I get rid of it ?

Thank you

cerbo gxVRMSmartShuntalarm
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·
@Steve

Check on the shunt itself if the auxiliary is configured for anything.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Steve avatar image Steve commented ·
Hi @Alexandra, thank you for your suggestion, you solved my problem. It was not the auxiliary but the high voltage alarm clear value on the device itself that was too low, 13V, I changed it for 14.5V