BSL Lithium Battery not Charging with Inverter, going to passthrough

Screenshot_2024-02-17-12-29-10-906_nl.victronenergy.jpgI have 15kwh BSL Lithium Battery (Slim Line) installed with 5kva 48V Multiplus I and Victron Smart MPPT 250/100 Tr using a Cerbo GX. I noticed the Inverter doesn't charge the battery when Grid is available, it will only do 'Passthrough", the MPPT only charges the battery during the day when Grid supply fails but will stop charging immediately Grid is restored. Please what is the solution to this.

MultiPlus Quattro Inverter Chargercerbo gxVictronConnectbslbatt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

Check that your meter is reporting as connected. If it has disconnected then the system will default to passthrough.

See the FAQ https://www.victronenergy.com/media/pg/Energy_Storage_System/en/faq.html#UUID-169dbd85-4b6f-814b-33c2-9fa77a6973d2_section-idm4628123204859232885885561444