Quattro II 48/5000 charger with LiFePo4 batteries BMS

In setting up our system it was clear that the MPPT charge controllers could be set to BMS control, and this works fine with the battery BMS connected to the BMS can port on the Cerbo… however it is unclear if the inverters also follow the BMS in charging from the generator. Is there a setting to make this happen, does it happen automatically, do you have to add an “Assistant“ I’ve been unable to find anything in the manual that indicates how to proceed. Thanks!

MultiPlus Quattro Inverter ChargerLithium BatteryBMS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

This is well documented in the dvcc guide, the manuals have all the info you need.

Any charging from any AC connection will be lead by the inverter under external control from the BMS.