MultiPlus II in parallel - ECO/Off mode

Hi,


I have recently set up two MultiPlus II 3000VA units in parallel to cover for periods of high load. I am wondering if it is supported to wire remote on/off of the slave unit to a relay and use assistants on the master unit to enable/disable slave based on the load.


Since both run in sync would it trigger alarms / problems when slave unit is off? I would then put assistant to start the slave on load going above 2000W.


Idle consumption of 3000VA is not very high +/-19W so I am not going to die over this, just curious if supported.


Thanks,

Marius.

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

As per the docs, the units operate as one device. If either is disabled, the whole system will stop. They do not operate independently and can't be configured as such.