question

christophlaib avatar image
christophlaib asked

Generator not delivering to Quattros

Hi all

got a 3 phase 7KW generator on AC1 of my Quattro II's.
When the generator is running, the grid input is switched of, and the installation gets the power from the battery. I see the quattros realize that there is AC from the generator, but they don't synchronize and axxept it.
- any advice ?

Generator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
delf67 avatar image
delf67 answered ·

Are the voltage and frequency of the generator's output within the correct range to match the settings in your Quattros? Are the Quattros set to "Ignore AC in?".

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Karlheinz Gosch avatar image
Karlheinz Gosch answered ·

Switch off the LOM in your Grid settings.

This should help accepting the Genset.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.