Multigrid not started after switched on

Hello,

My system consists of:

3 Multigrid 48/3000/35
1 Color Control GX
6 Pylontech US2000 Plus batteries

The Multigrid are installed for three-phase system out of the AC-OUT port.

I have followed the instructions from this documentation until including step 3:
https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

I want to continue with the configuration (step 4), but all three Multigrid did not start (i.e. none of the LEDs blink) after I switched them on. Note that a grid voltage of 230V can be measured at the AC-IN ports of the Multigrid.

What is causing this problem and how could it be solved? I would appreciate any help!

Thank you very much.

Pylontechmultigrid
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mohdisa avatar image
mohdisa answered ·

Update:

This simple problem (in hindsight) is solved as suggested in the Troubleshooting page. I unplugged the cable between CCGX and Multis first before I switched the Multis on.