New Victron energy meter (VM-3P75CT) the power for L1 is constantly wrong. The math doesn't make sense. 123V and 1.1 amps is not 14.9 watts. This just started happening a few days ago. I have a Carlos Gavazzi EM530 Connected to the exact same wires and location. EM530 When I installed the new meter a few weeks ago. The values matched each other. for a few weeks. I used Cerbo device list and a Custom Widget VRM graph to compare values. Unit is running the latest Firmware (1.05) The Cerbo GX is running latest firmware 3.14. I don't believe the Cerbo firmware has anything to do with this problem since the wrong values are seen in Victron connect, remote consol and VRM.

I did try loading old firmware on the energy meter (1.03) and Cerbo firmware 3.13 and 3.12 Reverting firmware did not fix the issue.

What can

1706670943621.png

1706671044594.png

1706671958738.png1706671063996.png

1706670933909.png1706672655148.png

1706672739647.png

Energy Meter
1706670933909.png (32.1 KiB)
1706670943621.png (40.4 KiB)
1706671044594.png (23.3 KiB)
1706671063996.png (50.3 KiB)
1706671958738.png (19.0 KiB)
1706672655148.png (20.2 KiB)
1706672739647.png (55.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
ldoes (Victron Energy) avatar image
ldoes (Victron Energy) answered ·

The reported current for the VM-3P75CT is the so called "RMS" current and the reported power is the so called "real" power. You might see a difference between the reported power and voltage * current, especially at low powers, because of low power-factor or distortion current in the system.

The value obtained from calculating voltage * current is called apparent power (in volt-amperes), and is always greater than or equal to the real power (in watts).

1708076491995.jpeg

That does not explain the difference between measured power for the VM-3P75CT and EM530 however. My best guess is that the current transformer on L1 is either broken, or not clamped correctly.


1708076491995.jpeg (41.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

filbo avatar image
filbo answered ·

I had similar problems and could not explain the values.
Phase L3 with over 2A should only supply a few watts? Makes no sense....

The solution was that the transformers (although the plastic clip was correctly closed) were not completely closed. After I additionally pressed them together with cable ties, it looks like the meter is delivering correct values.