Isolation transformer also corrects reverse polarity?

Will an isolation transformer also corrects reverse polarity? Is is self-polarizing?

Isolation Tranformer
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alex Pescaru avatar image
Alex Pescaru answered ·

The isolation transformer works with AC (alternating current).

There is no "reverse polarity" in AC because the polarity changes 50 or 60 times per second.

Or maybe I did not understood your question...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image
Kevin Windrem answered ·

OP is describing a reversed hot/neutral on the grid/shore power input.

Yes, the isolation transformer will isolate anything down stream of it from reversed hot/neutral.

However anything up stream of the transformer will still be subjected to line voltage on the neutral. Generally, the neutral conductor is not fused so any fault to safety ground could result in significant current flow and there may be no fuse/breaker to interrupt this current. It is advisable to fit the incoming power with a dual-pole breaker that will interrupt the neutral and hot conductors in the case of a fault.