ESS Multiplus disconnect AC-IN from Grid frequently for no reason

Hello,


ESS 3x Multiplus-II 48/3000 grid parallel with Pylonthech, Cerbo, RS 450/100, EM24

no AC-Out connected, no Grid connected solar inverter.

not the first system we have installed.

We have more ore less the same system running perfectly for a few month.

The AC-IN gets disconnected from grid after a minute for a few minutes for no reason over and over again.

everything ist brand new and FW is up to date....


Any ideas to solve the problem?






ESS
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

phoenix avatar image phoenix commented ·
Have you monitored the grid volts to see if they are dipping, or close to the limit. Might even be too high a voltage, particularly if you are a distance from the suppliers transformer with neighbours PV
0 Likes 0 ·
3 Answers
nickdb avatar image
nickdb answered ·

Connect with the mk3, under grid tab, check the NS protection log. It should store the last few outage events and the cause.

You could also use the VE bus monitor in real time which will show if there are grid issues.

Is there a smart meter? Some will disconnect if they see power being pushed.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Lars Filusch avatar image Lars Filusch commented ·
a EM24 rs485 grid meter
0 Likes 0 ·
Lars Filusch avatar image
Lars Filusch answered ·

the german grid is pretty stable, but i will take a look to the voltage as you mentioned.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Lars Filusch avatar image
Lars Filusch answered ·

Problem solved, bad neutral connection.