Hello,
I have 2 Victron 200Ah LiFePO4 Smart connected in series to a 24V System. After a couple of charging cycles to 100% SoC with my Multiplus 24/3000/70 I see via Victron Connect App that the 1st Bat (connected to Minus of Multiplus) has a perfect cell balancing. It has 3,37 / 3,36 / 3,36 / 3,37V so 1 mV max difference. The 2nd Bat which is connected to plus of the 1st Bat and Plus of the Multiplus is not well balanced. It shows 3,38 / 3,34 / 3,36 / 3,38 so 4 mv difference. I applied the method described in the Bat owners manual: charging w/ const current < 2,0A until Bat reaches 14,2 V. 14,2 V were reached after 1.5 hours. Balancing state at the end of this procedure was 3,53 / 3,55 / 3,59 / 3,59V so 6mv hence no success. Any idea what I have to do can do? Thanks for any hints.
Michael