Quattro gen on ac2in whant to set to only charger and no pass through

hallo

I have a setup where my quattro has connected a generator on AC2 IN, I would like it to only charge the batteries and let the inverter pull the load


how to set that in config???


best

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

That's not possible, you can't use AC IN (1 or 2) to charge and use the inverter at the same time.

Charging and inverting uses the same electronics.


img-20240110-180404.jpg


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2mas avatar image
2mas answered ·

Thanks for your respons :-)