I have an interesting issue with my off-grid setup:
- 2x 150/45 MPPT chargers
- 1x 100/20 MPPT charger
- 4x Pylontech US3000C batteries
- 1x Cerbo GX controller
- 2x Meanwell TS3000 inverters
- 1x Meanwell NTS450 inverter
Cable from the first Pylontech battery connected to the Cerbo GX, and the setup was working fine. However, yesterday, due to heavy rain, the battery got discharged below 10%. As a result, my home assistance system automatically turned off all non-critical loads (2x TS3000 inverters) and only kept running critical loads.(Meanwell NTS450 inverter)
Today, when I checked, the first battery in the stack (where BMS cable to Cerbo connected) had turned off, and the communication between the Cerbo GX and the battery was lost. The Cerbo GX displayed error #67, indicating a BMS connection loss, and all three MPPT chargers were also showing the same error, causing them to stop charging. This is fully off-grid setup with no other power source available. I have no way to check the battery's SOC, but my critical loads are still running. And later I saw the second battery of the stack also turned off.
To start charging the battery again, I disabled the DVCC (as there was no BMS control), and I had to reset the MPPT chargers to Non-BMS-controlled mode. Now MPPT chargers started working again. However, batteries 1 and 2 did not turn on automatically, while batteries 3 and 4 were on and charging.
My questions are: Do I need to wait for some time for batteries 1 and 2 to automatically turn on? Will the DVCC automatically turn back on?
My setup is monitored remotely, and there is no on-site personnel. I have a camera set up in the location where I can see the batteries and MPPTs
Appriciate your inputs