I have a digital multi control panel along with MultiPlus Compact 12/2000/80, what is the recommended setting for the current limit?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have a digital multi control panel along with MultiPlus Compact 12/2000/80, what is the recommended setting for the current limit?
It depends upon what the maximum current of your supply is. The idea of the Digital Multi Control is to limit the ammount of current that the MultiPlus takes when on weak shore connections.
The MultiPlus limits its self to within its own specifications if shore power is not limited or the limits are more than the MultiPlus could load it with.
White-paper-Achieving-the-impossible-EN.pdf @warnersw
i found this white paper explained the DMC and ho wit works very well
I have severe problems with the current limiter on my Multiplus 12/3000 and made some measurements with a stable load condition ~1300W :
with a limiter setting of 4-10A the AC1 will read 8.3 A, DC helps with ~7A.
with a limiter > 10A all load will come from AC1, battery is charging
with a limit < 4A all load will be switched to the battery.
Most camp-sites work with 5 or 6A cirquit-breakers, the Multiplus is not suited for the application.
I just changed from a 12/2000 to the 12/3000 because I thought the older 2000 had a problem, could have saved the money and the work.
OK, so i now checked some things, changed battery from "individual" to LiOn, set charge current to 120A and send the settings to the MultiPlus.
BUT, this time (for the first time) i didn't send only the modified, but ALL settings.
Now my AC-current limit is working, AND my DC-sense- wiring is working.
Thanks for nothing, Victron.