Ground relay in parallel unit configuration

Good morning everyone and of course Happy Holidays.

I managed to configure an MPII 5000 GX and an MPII 5000 in parallel. But I still had a doubt: should I leave the Ground Relay enabled on both units?

Config: Single Fase L1, "AC IN" connected together with Grid AC 230V, "AC OUT" connected together to Loads.

Ciao Manuele

multiplus in parallel
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fideri avatar image Fideri commented ·
0 Likes 0 ·
2 Answers
manuele avatar image
manuele answered ·

We are waiting for a response please...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

manuele avatar image
manuele answered ·

so as not to leave the thread hanging...

I confirm that the configuration of the ground relay must be made the same on all units in parallel (master and slaves).