Multiplus 48/5000 3 phase + 4x 16s lifepo4 connection

Can i connect 4 packs of 16s lifepo4 elements in parallel and the last pack to the distribution box or do i need to connect all 4 packs to distribution box?

battery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Ants Kosmos

All the batteries must be connected as one bank. So combined on one central bus bar.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Ants Kosmos avatar image Ants Kosmos commented ·

I think like this. Or one busbar, all these battery cables same lenght to bushbar and then 2 cables to distribution box ? I want build box for battery packs on wheels16s.png



V2.Do I still have to make the cables one length on the battery packs? They have separate BMS

16sv2.png