I try to change the minimum V for shut down for my Multiplus 24/5000/120-100 which is set too high. I get a .vrsc file and then the Victron Conect for Windows only opens .vcsf. What can I do?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I try to change the minimum V for shut down for my Multiplus 24/5000/120-100 which is set too high. I get a .vrsc file and then the Victron Conect for Windows only opens .vcsf. What can I do?
Did you download the settings from VRM?
If yes you need to use VE.config to open, edit and save them.
https://www.victronenergy.com/live/vrm_portal:remote-veconfigure