SmartSolar MPPT temperature source with both SBS and BMV on VE smart network

I would like to install a SmartSolar MPPT and a BMV in my RV for the house battery bank. I would also like to install an SBS to provide temperature to the MPPT for compensation while sensing starter battery voltage at B2 on the BMV shunt. However I have seen some writings that seem to indicate that this will not work because when a BMV is in the network the MPPT only looks for temperature input at B2 of the shunt and ignores the SBS temp info. Meaning, if I want temperature compensation and I have a BMV in the network my only choice is to use B2 for temperature and not voltage. Is this correct or would my original plan using the SBS for temp and B2 for voltage work?

temperature
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mark avatar image
Mark answered ·

You can get it to work by leaving the BMV out of the network and only having the MPPT & SBS in the VE.Smart Network.

The SBS will then provide BOTH voltage & temperature to the MPPT.