Phoenix inverter 250VA on MPPT 100/20

Hello,

Would connecting Phoenix 250VA directly to Load terminals of MPPT 100/20 (with connected battery of course) work or start curent draw peak from inverter will trigger solar controler's overcurrent protection? The load on the inverter would be 150W max and the battery is LiFePO.

MPPT ControllersPhoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
djsmiley avatar image
djsmiley answered ·

No. Load output is not suitable for loads like an inverter.

https://www.victronenergy.com/media/pg/Manual_SmartSolar_MPPT_75-10_up_to_100-20/en/features.html#UUID-c2b1f357-ff37-9fae-5bfa-a8ba2185fd92

Some loads, particularly inverters, have a higher current rating or high start-up current rating, exceeding the load output's capacity. These loads should be connected directly to the battery.