2 units of Quattro 15kva =30kva with another of 4 nos of smart-solar 250/100 with an additional 75kwh open loop communication (generic lithium, no CAN PORT connection).
what can I do to eliminate the frequent passthru mode?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
2 units of Quattro 15kva =30kva with another of 4 nos of smart-solar 250/100 with an additional 75kwh open loop communication (generic lithium, no CAN PORT connection).
what can I do to eliminate the frequent passthru mode?
@fasami oluwaseun Several questions.....
Do you have a grid meter fitted?
Do you have anything connected to the AUX connections?
Are you using an ESS assistant?
Do you have any manual overrides set?
Do you have an export of your VE Configure settings you can share?
Do you have a grid meter fitted? NO
Do you have anything connected to the AUX connections? NO
Are you using an ESS assistant? YES
Do you have any manual overrides set? NO
how do I go about this?
I don't have the export of your VE Configure settings.
is it acceptable to share the link to the site with you?
For example, I have attached a copy of mine.
Any links you share should be read only information.
TAB: General
System frequency 50Hz
Shore current 50.0 A
Overruled by remote checked
Secondary input shore current 16.0 A
Overruled by remote checked
Dynamic current limiter checked
State of charge when Bulk finished 95.0 %
Battery capacity 1750 Ah
Charge efficiency 0.95
TAB: Grid
Country / grid code standard None: (feeding energy from DC to grid not allowed)
Accept wide input frequency range (45-65 Hz) checked
AC low switch mains off 180 V
AC low switch mains on 187 V
AC high switch mains on 265 V
AC high switch mains off 270 V
UPS function checked
TAB: Inverter
PowerAssist unchecked
Inverter output voltage 230 V
Ground relay checked
Inverter DC shut-down voltage 50.50 V
Inverter DC restart voltage 52.50 V
Low DC alarm level 52.00 V
Do not restart after short-circuit (VDE 2510-2 safety) unchecked
enable AES unchecked
TAB: Charger
Enable charger checked
Weak AC input checked
Stop after excessive bulk checked
Lithium batteries checked
Disable VSense (for diagnostic purposes) unchecked
Configured for VE.Bus BMS unchecked
Charge curve Fixed
Absorption voltage 55.20 V
Float voltage 55.00 V
Charge current 100 A
Repeated absorption time 1.00 Hr
Repeated absorption interval 7.00 Days
Absorption time 1 Hr
TAB: Virtual switch
TAB: Usage
Virtual switch usage Do not use VS
TAB: Assistants
TAB: Assistant Configuration
generator start and stop (size:186)
*) Use the general flag
*) Open relay to start generator.
*) Start generator when DC input voltage
is lower than 52.50 volt for 30 seconds.
*) Stop generator when DC input voltage
is higher than 54.00 for 120 seconds.
*) The generator is not stopped by AC input.
general flag user (size:5)
*) Use general flag to ignore AC input 1
Total size of all assistants including the required
(hidden) system assistants is: 260
@fasami oluwaseun You mentioned you have a ESS assistant set up but am I correct in saying you are connected to a generator, or is that just a profile you have set up to avoid polling from the grid with a contactor? I do not see your ESS assistant settings in the above.
In your settings, you have 'Inverter DC restart voltage 52.50 V' but your bettery is 52.4v therefore your inverter will not operate with the current battery voltage and the settings you have. IF the PV is not charging the batteries, and you have no charge settings to the betteries, your Multiplus will be stuck in 'passthru'.
we set the ESS assistance at the initial stage but on the occurrence of the pass-thru mode, we had to override by unchecking the ESS.
Yes, set the inverter DC restart voltage to 52.50v but the diffident levels of battery voltage like 52.6,52.7, etc the pass-thru keeps occurring.
PLEASE...kindly guide me on what to do based on this info and export report of my VE Configure setting.
even, I also experienced pass-thru today again. am worried about this?
kindly find the screenshot of today's event.
I NEED TO RESOLVE THIS PROBLEM ....PLS GUIDE ME.