question

toadhill avatar image
toadhill asked

24 Volt Temperature Compenaation

I have a Smart Solar 150/45 24v controller. It asks for an entire bank temp compensation value. Kilovault 2100 PLC requires -30mv/degree Celsius or -5mv per cell/ degree Celsius. Do I enter -30 or -60 in the Temp Comp parameter. I didn’t know if the charger automatically double the value for you.. Thanks

temperature compensation
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

Still using lead batteries?

24V bank is 12 cells in series, so temp compensation is -60mV/C. This is the value to set the MPPT at.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

toadhill avatar image toadhill commented ·
Kilovault Carbon AGM. (2100 PLC)
0 Likes 0 ·