Multiplus-2 is power assisting even when power assist is disabled in settings

Hello. I'm using a Multiplus-2 48/5000/70-50 running 507 firmware and noticed that it sometimes disconnects itself from the grid and I can see in VRM that it was doing the power assist even though I have it turned off and set input current limit to 32 A (230 V) which is way more than it was necessary to run a 2 kW load that you can see on the screenshots.
So the main question is why does the power assist happen when it is disabled in settings?
Thank you.victron-connect.pngvrm.pngvrm-2.png

Multiplus-IIpowerassist
victron-connect.png (294.1 KiB)
vrm.png (163.7 KiB)
vrm-2.png (106.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Rost

You may have a high impedence connection to grid, so the easier source is the battery. The disconnect from grid is a symptom of that.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rost avatar image rost commented ·

@Alexandra

That certainly can be the case. Some time ago I asked a question on this forum regarding random disconnects from the grid that I still experience at this thread

Sadly, as far as I can tell, there are no diagnostic logs in MP-2 apart from NS protection log that can tell why the disconnect happened.

Is there a way to read a resistance of grid connection measured by MP-2?

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ rost commented ·

Changed resistance to impedence. The more correct term.

No I don't think the inverter or system does records/reports it anywhere. I have not really looked to be honest.

You can sometimes tell a connection problem by the way the voltage and frequency fluctuate

If you pull a high amp draw from there does the voltage sag? If it does the connection impedance is high.


0 Likes 0 ·