I'm getting confused. I can't find the temperature compensation value for the AGM Super Cycle battery.
It says that the recommended temperature compensation for Victron VRLA batteries is -4 mV/cell (-24 mV/°C for a 12V battery).
So I deduce that these are the values that should be applied to the MPPT charger? Is this correct?
What I find strange is that when I choose the AGM parameters on the MPPT charger, the default values are always -16.2 mV/°C.
These default parameters should be set to -24 mV/°C when choosing this type of battery, shouldn't they?