Problem with Victron Mutliplus 800va Compact

Dear Community,

I recently bought:

1. Victron Mutliplus 800va Compact (plastic and not the big metal one)

2. Redondo Mini 12v 100ah battery

3. Victron SmartShunt 500a/50mv

4. The necessary mega fuse for the connection.

The purpose of the mutliplus is to operate as a UPS and support two storage devices and other smaller electronics. The storage devices are also supported by a APC ups that is connected to the Victron.

The Victron inverter is connected to grid power. (230v in Greece)

The problem I phase is the following:

Although the battery shows 100 charged (which is a per the manual from redondo which states that if the voltage is higher than 13.33v the battery is considered as 100% charged) when I activate the charge function on multiplus, the inverter tries to Bulk charge the battery and ends up connecting and disconnecting to the grip. When it changes to Absorption or Float then everything works ok without any connecting or disconnecting. It is only when it tries to Bulk charge a full battery that the problem occurs.

If the connecting disconnecting happens multiple times in a row I also receive a warning for Battery voltage ripple.

screenshot-20231116-142401.jpg

When I disable charging everything works as normal.

I am attaching screenshots of the parameterization of the inverter:

2-screenshot-20231116-142607.jpg

3-screenshot-20231116-142638.jpg

4-screenshot-20231116-142710.jpg

6-screenshot-20231116-142739.jpg

7-screenshot-20231116-142747.jpg

8-screenshot-20231116-142759.jpg

Below a screenshot from the smartshunt while not charging

smartshunt-while-not-charging.jpg

Has anybody faced similar issue and are the settings for the battery ok?

Currently I have disabled charging so no on/off connecting to grid.

Thank you all in advance.


multiple inverters
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
kevgermany avatar image
kevgermany answered ·

I'm not sure what the battery makers recommend, it will be in the manual. But the charge settings (absorption/float) in the inverter look to be the problem, as in too high. This causes the BMS to disconnect the battery for safety.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ctsit avatar image
ctsit answered ·

@Alexandra @kevgermany

I did all the changes but still the same issue, it connects and disconnects from the grid rapidly.

And again I get a battery voltage ripple.

I had to disable the charging again to avoid the repeating connect and disconnect.

Obviously I am doing something wrong but I cant get my head around to what.

Any other ideas?

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ctsit avatar image
ctsit answered ·

I am using 25mm2 cables, as per the specification.

Everything is tide down very well both on the inverter side, battery side but also the shunt and fuse (will try check again though)

As a fuse I use the victron 60amp since I don't think I will go over that.

Lastly the over all length of the cable is about 2m for each positive and negative and is including the segment between battery and fuse and battery and shunt.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ctsit avatar image
ctsit answered ·

Furthermore, I noticed that as long as the charge voltage remain under 13.98v then the system charging works normally.

As soon as it goes over 13.99v then cuts off grid power and I get the Voltage Ripple message, more specifically I reduced the charge current to 1amp and noticed that the system didn't cut off grid until the charge voltage was more than 13.98v.

After a while the charge changed to absorption and now that I change the current back to 20amp there is no disconnect from grid due to the absorption state.

15 comments