I have an off-grid system with 4 x Trinasolar 405W – 11.77A (Imp) – 41.4V (Voc) Panels wired as 2 x Series strings. Each string connected to a Victron BlueSolar MPPT 60A/150V charge controller MC4. Both controllers feeding four Rolls 6v S6-L16 Batteries (24v series) going to Victron Multiplus 24/3000/70-50.
Yesterday I checked the system, with batteries fully charged (in storage mode) and noticed that one of the charge controllers was in float and the other showed the bulk LED blinking slowly. I tested the panel voltage to each controller and the one with the blinking LED was receiving zero voltage (other controller fine at 70+ volts). So, I switched off the panels at the circuit breakers before the controllers and, surprisingly, when tested, both sides were producing voltage around 70V… as soon as I switched breakers back on – no voltage to the blinking controller!
I have ordered a VE Direct Bluetooth Dongle so I can then connect and look for error codes etc. But I wondered if anyone could offer an explanation?