billys1337 asked

VE config pre-alarm/shutdown voltages

Hey all,
Quick question, that is, when a multiplus in DVCC reaches its shutdown, pre-alarm, restart voltage thresholds, what voltage source is triggering this, the DVCC voltage (ie. a smart shunt)? or voltage at the multiplus?
Secondary question, a low voltage alarm mark on the chart (Warnings and Alarms) from the multiplus that shows in VRM , is this alarm triggered based on the pre-alarm voltage set in VE Configure? DVCC? smart shunt? or something else?

Thanks for any help :)

MultiPlus Quattro Inverter Chargerbattery system voltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@billys1337

Is the system BMS controlled? If not, then it is the inverter settings. Either the ones in ESS or the low voltage pre alarm.

In the VRM the device it came from will tell you on the alarm