dac07800 asked

Cerbo GX Alarm Rule for Generator Run Time?

Is there a way to trigger an alarm in the Cerbo GX every time the generator (AC input 2) hits 500 hours? This will assist in servicing the generator etc.


TIA

cerbo gxGeneratoralarm
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Arne Parneby avatar image
Arne Parneby answered ·

Yes, under generator start/stopcerbo-generator-service.png