I have an issue on a new install where the customer already had a generator and wanted it integrated into the system.
The generator is a Hyundai DHY8000 rated at 5500W continuous and connected at 230v single phase. I was planning to set the AC input limit at 20 amps, so around 4600W, but I cant get a reliable connection at anything over 7 or 8 amps.
I have load tested the generator at around 4.5KW using other loads and it functions correctly.
If I have the Multiplus connected with only lighting loads of around 300W and set an input limit of say 10 amps it connects, starts to charge then after a time disconnects from the generator and runs the lighting loads from the inverter. The Multiplus also omits a kind of vibrating sound I assume from the transformer / coil inside.
I assume the issue is to do with the fact that the Multiplus (in charger mode) is a non resistive load but I would still like to try and resolve the issue.
Any ideas or opinions gratefully accepted.