why is my victron inverter output breaker tripping after 30 mn and the inverter goes off and the battery still on

inverter current draw
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
abrahamsolar avatar image
abrahamsolar answered ·

Hi from the USA, @yanmpoyi. When the inverter turns off, are you seeing the Overload red LED lit solid? If so...and especially if the output AC wiring has been newly installed or recently modified...here's a theory:

Wires can move a bit when they heat up & your wires may be moving enough to develop an AC short circuit which then goes away when they cool down. Inverters often do an overload shutdown quicker than the AC circuit breaker can trip but in your case both reactions may be occurring around the same time.

I'd look for a "hot" that's somehow managing to brush ever so lightly against the metal chassis or wiring box. A tiny contact is enough.

Sunny Days~